Forum Discussion
Hi Nick,
Is your DataCentre/Comms room over 40 Degrees? I think it would be prudent to stick to manufacturers guidelines for heating alerts, rather than adjust them to stop alerts being raised.
The other alternative is to configure Nagios to ignore anything below your threshold (If you feel that confident...)
Dear Iain , No actually the data center is cooled efficiently ( has a stable 23 degrees Celsius ) but the location where the specific rack with the LB is in the position where it doesn't get optimal cooling ( also that rack happens to be full). So i was wondering since it spikes for a short period of time to 41 ,42 or 47 the highest with the fans not even working full speed at 20k ( mostly around 16k rpm ) maybe to increase the Nagios threshold to avoid that. As no expert in F5 thought better to ask first.